Re: Solar Energy, A Complement To FTA by Milito: 11:43pm On May 22, 2023
Jefferyzz:
Yes you can. But if ur choice of battery is a 12v Lead acid, don't do more than d c rating inside d batteries manual or on d body. If your going for lifepo4. Ur battery can safely go as high as 1c. But that doesn't mean you should load ur inverter pass 60-70% of it's actual capacity. U will break it in no time.

What is C rating please?

Any clue from the attached pic?

Re: Solar Energy, A Complement To FTA by Milito: 11:48pm On May 22, 2023
earthrealm:


its ok, but doesn't make sense...its like using a bike to move from lagos to abuja, vs using car
why do you think you need a 7.5kva inverter, the bigger the inverter the bigger its self consumption energy

The inverter is just to backup lights and computers in a workplace until change over to gen and vice versa (less than 5mins at different times throughout the day only).

A number of the lights are halogen spotlights with high energy consumption; which was why the load Audit recommended 7.5KVA. The 4 unit battery is to save cost in view of the small backup time required.
Re: Solar Energy, A Complement To FTA by gadgetplanetng: 7:27am On May 23, 2023
Won't an 8kva UPS serve better in this case?

Milito:


The inverter is just to backup lights and computers in a workplace until change over to gen and vice versa (less than 5mins at different times throughout the day only).

A number of the lights are halogen spotlights with high energy consumption; which was why the load Audit recommended 7.5KVA. The 4 unit battery is to save cost in view of the small backup time required.
Re: Solar Energy, A Complement To FTA by zeestone99(m): 7:58am On May 23, 2023
Sunmart vmii 5.5kw 48v 100a hybrid inverter 500vdc - 375k

Sunmart Vmii 3.5kw 24v 100a hybrid inverter 500vdc - 320k

Sunmart Vmiii plus 3.5kw 24v 100a hybrid inverter 500vdc - 340k

Sunmart Vmiii plus 5.5kw 48v 100a hybrid inverter 500vdc - 395k

Sorotec Revo Vmii 5.5kw 48v 100a hybrid inverter 500vdc - 420k

Sorotec Revo Vmii 3.5kw 24v 100a hybrid inverter 500vdc - 340k

Sorotec 5.5kw 48v 100a hybrid inverter 500vdc parallel version (includes parrallel kit) - 460k

Sorotec 3.5kw 24v 100a hybrid inverter 500vdc parallel version (includes parrallel kit)- 380k

Sorotec Revo vmiii 5.5kw 48v 100a hybrid inverter 500vdc - 440k

Sorotec Revo vmiii 3.5kw 24v 100a hybrid inverter 500vdc - 360k

Powmr 3.2kva 24v 80a 450vdc mppt hybrid inverter - 250k

Powmr 3.5kva 24v 100a 500vdc mppt hybrid inverter - 340k

Powmr 5.5kva 48v 100a mppt hybrid inverter - 385k

Snadi 3.5kva 24v inverter wall mount (transformer) - 270k

Snadi 5.5kva 24v inverter wall mount (transformer) - 345k

Snadi 5.5kva 48v inverter wall mount (transformer) - 345k

Epever tracer 60a mppt charge controller - 175k

Epever tracer 100a mppt charge controller - 280k

Must 100a mppt solar charge controller - (out of stock)

Must 60a mppt solar charge controller - 130k

Must 80a mppt solar charge controller - 140k

Fangpusun flexmax 80a mppt charge controller - 270k

Fangpusun flexmax 60a mppt charge controller - 200k

Fangpusun 50a 12/24v - 90k

40amps mppt lumiax Bluetooth controller - 80k

60amps lumiax Bluetooth mppt controller - 145k

60amps 12/24/36/48v powermr mppt - 80k

Greenpole 48v 100ah lithium battery - 950k(out of stock)

Avr/current limiter 60a (Tomzn) - 9k

Avr/current limiter 63a 4pole (tomzn) - 23k

Change over breaker/MTS - 5k

Change over breaker/MTS 4pole - 15k

DC SPD 500v - 8k

DC SPD 500v (Tomzn) - 8.5k

DC spd 1000v (tomzn)- 9k

Ac spd 385v - 7k

Ac spd 275v (tomzn) - 8k

Ac spd 4 pole - 15k

DC Voltmeter (5v- 120v ) - 1.5k

DC Voltmeter (8v- 100v / with battery indicator and %) - 4k

Watt meter - 15k

Mc4 connectors - 550

Mc4 y connector 2 in 1 - 2.8k

Mc4 y connector 3 in 1- 3.5k

Mc4 y connector 4 in 1 - 8k

Programmable timer 15a UK pkug - 9k

Programmable timer 25a - 9k

solar DC fuse holder 1 pole (tomzn) - 3k

Solar DC fuse holder 2 pole (tomzn)- 5.5k

Solar DC fuse (10a/16a/20a/25a/30a) - 1.5k

DC breaker 10a 600v double pole (tomzn)- 5k

DC breaker 16a 600v double pole (tomzn) - 5k

DC breaker 20a 600v double pole (tomzn) - 5k

DC breaker single pole (32-63a) - 3k

DC breakers double pole 63a - 5k

DC breaker double pole 100a - 8k

Dc breaker double pole 125a - 9k

DC breaker double pole 100a (tomzn)- 9k

Dc breaker double pole 125a (tomzn)- 10k

Dc breaker mccb 250a double pole - 23k

Ac breaker double pole 10a (Tomzn)- 3.5k

Ac breaker double pole 16a (Tomzn)- 3.5k

Ac breaker double pole 32a (Tomzn)- 3.5k

Ac breaker double pole 63a (Tomzn)- 3.5k

Ac breaker double pole 10a (Chint)- 3.5k

Ac breaker double pole 16a (Chint)- 3.5k

Ac breaker double pole 32a (Chint)- 3.5k

Ha02 battery balancer - 35k

Busbar (Red and Black) - 20k

Automatic transfer switch (ATS) 63a (wall mount) - 24k

Automatic transfer switch (ATS) 63a (tomzn) - 21k

Automatic transfer switch (ATS) 100a (tomzn) - 22k

Automatic transfer switch (ATS) 125a (tomzn) - 24k (out of stock)

Automatic transfer switch (ATS) 100a 3phase 4 pole (tomzn) - 35k (limited quantity)

6 in 1 Ac display meter ( watts, voltage,kWh,amps, freq, power factor) - 15k

6way breaker enclosure - 3.5k

9 way breaker enclosure - 4.5k

12way breaker enclosure - 5k

DM for other items.

Call/chat - 08117398294

Re: Solar Energy, A Complement To FTA by Jefferyzz(m): 9:39am On May 23, 2023
This discharge rating is quite low. It's states 200a discharge is 20hrs that's 0.1c or 10% of the capacity in 1hr. Probably that's just a paper something. Cause batteries like fullriver should be able to handle atleast 30% or 0.3c eg a discharge of 60a of dat 200a in 1 hr. It's not like I av fullriver batteries but I av 2 quanta SLA n dey do 30% of capacity discharge. Well. It best you stick to wat u av on the battery. So as not to kill it b4 it time
Milito:


What is C rating please?

Any clue from the attached pic?
Re: Solar Energy, A Complement To FTA by odimbannamdi(m): 9:53am On May 23, 2023
emmy9500:
Is this type of charge controller suitable to charge a 5kw/24V lithium battery

Yes bro. It is a dedicated profile for lithium charging. You just have to set the parameters

Re: Solar Energy, A Complement To FTA by samir101ng(m): 11:16am On May 23, 2023
brightk:
Btw jinko and Canadian panels which is better.. Apart from gennex, any reliable seller for original canadian panels

Techland Solar is also a reputable seller of Canadian Solar Panels. Canadian Solar panels are slightly above the average than Jinko but they are all Tier 1 rated panels with authorized dealers in the country so you can't go wrong with either one.

2 Likes

Re: Solar Energy, A Complement To FTA by papiTwist: 8:19pm On May 23, 2023
Hello Good People,

My 5kva/48v inverter suffered lightning damage a few weeks ago. I’ve spent some reasonable amount of money in the course of the repair, and I wouldn’t want to have a similar experience again.

Please I need a help on how best I can protect the inverter from lightning damage. I would appreciate any device (with price) that can help me achieve this protection.

Thank you all in anticipation to your kind response.
Re: Solar Energy, A Complement To FTA by funshyboi(m): 12:27am On May 24, 2023
Please is anyone familiar with this charger. It’s LiFePO4 battery charger. Who has the idea of where I can get it fixed in Lagos

Re: Solar Energy, A Complement To FTA by oloet: 6:12am On May 24, 2023
funshyboi:
Please is anyone familiar with this charger. It’s LiFePO4 battery charger. Who has the idea of where I can get it fixed in Lagos

I will advise that you buy a new one rather than repair because how sure are you that the charger is going to be optimal after repair

1 Like

Re: Solar Energy, A Complement To FTA by samir101ng(m): 9:45am On May 24, 2023
papiTwist:
Hello Good People,

My 5kva/48v inverter suffered lightning damage a few weeks ago. I’ve spent some reasonable amount of money in the course of the repair, and I wouldn’t want to have a similar experience again.

Please I need a help on how best I can protect the inverter from lightning damage. I would appreciate any device (with price) that can help me achieve this protection.

Thank you all in anticipation to your kind response.

This has been discussed extensively some pages back and on the DIY Nigeria Telegram group. A lot of times people forget or overlook the safety aspect of their installations forgetting that Sango, Thor & Amadioha belong to the same whats app group and start doing press up during the rainy season looking for who's inverter to smite. For any basic installation you are first and foremost expected to have a functional earth system installed in your house. You may be using an ELCB or RCCB depending on what was installed. Test it and ensure that it is functional by a qualified electrician. You may wish to also install a lightning arrestor to serve as an potential pathway for any strikes Thor might send your way. Finally for your system, you are expected to install Surge Protection Devices (SPD) at both the DC side from your charge controller and AC side input from the grid. This can significantly help your chances of recovery from an indirect strike. But ultimately there is nothing you can do to prevent any damage from a direct strike on your house. You can order directly online from AliExpress or from some of the retailers here advertising on the thread. Hope this helps a bit.

3 Likes

Re: Solar Energy, A Complement To FTA by papiTwist: 11:49am On May 24, 2023
samir101ng:


This has been discussed extensively some pages back and on the DIY Nigeria Telegram group. A lot of times people forget or overlook the safety aspect of their installations forgetting that Sango, Thor & Amadioha belong to the same whats app group and start doing press up during the rainy season looking for who's inverter to smite. For any basic installation you are first and foremost expected to have a functional earth system installed in your house. You may be using an ELCB or RCCB depending on what was installed. Test it and ensure that it is functional by a qualified electrician. You may wish to also install a lightning arrestor to serve as an potential pathway for any strikes Thor might send your way. Finally for your system, you are expected to install Surge Protection Devices (SPD) at both the DC side from your charge controller and AC side input from the grid. This can significantly help your chances of recovery from an indirect strike. But ultimately there is nothing you can do to prevent any damage from a direct strike on your house. You can order directly online from AliExpress or from some of the retailers here advertising on the thread. Hope this helps a bit.


Thanks for your help.
Can you please send me the link to join the DIY Nigeria telegram group on 07035383828.

Secondly, will the ratings on the pictures you attached be perfect for protecting 5kva/48v inverters?
Re: Solar Energy, A Complement To FTA by samir101ng(m): 1:49pm On May 24, 2023
papiTwist:



Thanks for your help.
Can you please send me the link to join the DIY Nigeria telegram group on 07035383828.

Secondly, will the ratings on the pictures you attached be perfect for protecting 5kva/48v inverters?

Done sir. As for whether the SPD listed are sufficient for a 5kva/48v system, i suggest you contact your installer and read up more on the different brands and options available.
Re: Solar Energy, A Complement To FTA by funshyboi(m): 2:02pm On May 24, 2023
oloet:


I will advise that you buy a new one rather than repair because how sure are you that the charger is going to be optimal after repair

Been looking for where to buy but didn’t see.
If anyone can recommend this particular around Lagos I will appreciate
Re: Solar Energy, A Complement To FTA by Loneley: 10:08pm On May 24, 2023
Hi guys, I'll appreciate your opinion on this.

Picture 1 shows my inverter's battery indicator with the battery full.

And picture 2 shows the battery when external power is cut off, it drops to almost half.

The installer would come check it out on Saturday, but before he does, I would like to have an idea of what's responsible.

The system was set-up about a week ago.

Re: Solar Energy, A Complement To FTA by earthrealm(m): 10:44pm On May 24, 2023
Loneley:
Hi guys, I'll appreciate your opinion on this.

Picture 1 shows my inverter's battery indicator with the battery full.

And picture 2 shows the battery when external power is cut off, it drops to almost half.

The installer would come check it out on Saturday, but before he does, I would like to have an idea of what's responsible.

The system was set-up about a week ago.

the dropping to half, is it with load or no load?

but first off, those battery level indicators can be error prone. best you use a digital meter to test the voltage at the 2 different times. is the battery flooded type?
Re: Solar Energy, A Complement To FTA by zeestone99(m): 11:27pm On May 24, 2023
papiTwist:
Hello Good People,

My 5kva/48v inverter suffered lightning damage a few weeks ago. I’ve spent some reasonable amount of money in the course of the repair, and I wouldn’t want to have a similar experience again.

Please I need a help on how best I can protect the inverter from lightning damage. I would appreciate any device (with price) that can help me achieve this protection.

Thank you all in anticipation to your kind response.

Lightning arrestor and surge protective devices are all u need
Re: Solar Energy, A Complement To FTA by Loneley: 1:43am On May 25, 2023
It's with no load, and the batteries are tubular.


earthrealm:


the dropping to half, is it with load or no load?

but first off, those battery level indicators can be error prone. best you use a digital meter to test the voltage at the 2 different times. is the battery flooded type?
Re: Solar Energy, A Complement To FTA by olopan(m): 9:12am On May 25, 2023
Sorry to hear about your loss and the aftermath expenses.

There are two ways to which power comes in through you inverter

1. Solar
2. Nepa/grid

Your protection for surge needs to come into play at these two areas.

Example here is if you're using a 500Vdc charge controller
You need something close enough to this
E.g. a 500Vdc/550 Vdc clamping protector
Or a 275Vac protector for NEPA

If going for premium SPD e.g. Midnite best to have over 200k for both
If average ones like explained above e.g. from china

contact these places/people to get your SPD

Techland, solar shop, saipro from this forum or me( I will only source for you)
papiTwist:
Hello Good People,

My 5kva/48v inverter suffered lightning damage a few weeks ago. I’ve spent some reasonable amount of money in the course of the repair, and I wouldn’t want to have a similar experience again.

Please I need a help on how best I can protect the inverter from lightning damage. I would appreciate any device (with price) that can help me achieve this protection.

Thank you all in anticipation to your kind response.
Re: Solar Energy, A Complement To FTA by ojesymsym: 11:53am On May 25, 2023
Lightning arrestor and surge protective devices are all u need a good place to start.
zeestone99:


Lightning arrestor and surge protective devices are all u need
Re: Solar Energy, A Complement To FTA by CAROLYN19: 12:34pm On May 25, 2023
Are you in need of Industrial Power Solution Equipment such as Automatic Voltage Regulator (AVR), Emerson/Vertiv UPS , Inverters and Gaston Battery? Call/Watsapp us on 08066332919. We have Offices in Lagos and Abuja. We do Nationwide Delivery.

Re: Solar Energy, A Complement To FTA by dollarnaira: 2:00pm On May 25, 2023
Loneley:
Hi guys, I'll appreciate your opinion on this.

Picture 1 shows my inverter's battery indicator with the battery full.

And picture 2 shows the battery when external power is cut off, it drops to almost half.

The installer would come check it out on Saturday, but before he does, I would like to have an idea of what's responsible.

The system was set-up about a week ago.

Is your inverter GSR?
Battery as Tubular?
Re: Solar Energy, A Complement To FTA by Loneley: 2:25pm On May 25, 2023
Yeah, it is.

The battery is also GSR

dollarnaira:


Is your inverter GSR?
Battery as Tubular?

Re: Solar Energy, A Complement To FTA by dollarnaira: 3:02pm On May 25, 2023
Loneley:
Yeah, it is.

The battery is also GSR

Tubulars need the right amount of charging current and voltage ( the voltage especially).

Check the sticker on the battery for better information.
Re: Solar Energy, A Complement To FTA by Loneley: 3:36pm On May 25, 2023
Will do when I get home, thanks.

Still, it doesn't matter how long it charges full from the panels or public power, like for example, last Sunday, there was light throughout.

Yet, once they took the light, battery indicator immediately dropped by almost half.


dollarnaira:

Tubulars need the right amount of charging current and voltage ( the voltage especially).

Check the sticker on the battery for better information.
Re: Solar Energy, A Complement To FTA by dollarnaira: 3:59pm On May 25, 2023
Loneley:
Will do when I get home, thanks.

Still, it doesn't matter how long it charges full from the panels or public power, like for example, last Sunday, there was light throughout.

Yet, once they took the light, battery indicator immediately dropped by almost half.

Get a Dc meter to check.
Or a voltmeter.


Re: Solar Energy, A Complement To FTA by dollarnaira: 4:08pm On May 25, 2023
Loneley:
Will do when I get home, thanks.

Still, it doesn't matter how long it charges full from the panels or public power, like for example, last Sunday, there was light throughout.

Yet, once they took the light, battery indicator immediately dropped by almost half.

Get a Dc meter to check.
Or a voltmeter.
Are u on 12 or 24v system?
Re: Solar Energy, A Complement To FTA by Loneley: 7:44pm On May 25, 2023
I will, bro, thanks.

You've been helpful.

It's a 24V system. Attached is a photo of the setup


dollarnaira:


Get a Dc meter to check.
Or a voltmeter.
Are u on 12 or 24v system?

Re: Solar Energy, A Complement To FTA by Hollawayn05(m): 8:33pm On May 25, 2023
Greetings great minds
My inverter has been acting funny, works normal since i installed, I usually charge with panels alone for about a month till the devilish nepa reinstall the power grid, on the first day I charged with nepa light during the day, then at night when I started using with load less than 0.007% for 30 min it started giving signal for low battery, upon checking the inverter the bat voltage has dropped to 11.6 while the charge control was still on 12.2, if i off and on after some minutes the inverter comes back to 12.3 or above and the cycle continues..

This has been happening for 3 weeks now,

Someone pls come to my aid

Details
Inverter :new famicare 1.5kva
Battery : luminous 220am
Charge controller : powmr 60apms
300 watt x2
Re: Solar Energy, A Complement To FTA by earthrealm(m): 8:59pm On May 25, 2023
Hollawayn05:
Greetings great minds
My inverter has been acting funny, works normal since i installed, I usually charge with panels alone for about a month till the devilish nepa reinstall the power grid, on the first day I charged with nepa light during the day, then at night when I started using with load less than 0.007% for 30 min it started giving signal for low battery, upon checking the inverter the bat voltage has dropped to 11.6 while the charge control was still on 12.2, if i off and on after some minutes the inverter comes back to 12.3 or above and the cycle continues..

This has been happening for 3 weeks now,

Someone pls come to my aid

Details
Inverter :new famicare 1.5kva
Battery : luminous 220am
Charge controller : powmr 60apms
300 watt x2

YOUR battery is weak, either the electrolyte sg is wrong, or you inverter and charge controller isnt giving the battery the correct charging voltage. check that ur charge controller is configured to send 14.7volts to the battery. your inverter is a dumb inverter..so you cant change the charge voltage---.

how many amps or watts do you see on the charge controller at midday in bright sunlight?...or attach a picture of the charge controller screen if you dont know what am asking
Re: Solar Energy, A Complement To FTA by Hollawayn05(m): 10:06pm On May 25, 2023
earthrealm:


YOUR battery is weak, either the electrolyte sg is wrong, or you inverter and charge controller isnt giving the battery the correct charging voltage. check that ur charge controller is configured to send 14.7volts to the battery. your inverter is a dumb inverter..so you cant change the charge voltage---.

how many amps or watts do you see on the charge controller at midday in bright sunlight?...or attach a picture of the charge controller screen if you dont know what am asking

Thanks sir
The charge controller shows above 13amps and 200watt at peak period and how do I configure my cc to give 14.7V?
Re: Solar Energy, A Complement To FTA by earthrealm(m): 7:53am On May 26, 2023
Hollawayn05:


Thanks sir
The charge controller shows above 13amps and 200watt at peak period and how do I configure my cc to give 14.7V?


Read the manual that came with your CC and change the settings.
200w /13amps @ peak from 2 x 300watts panels is very poor. Something is wrong. Get a pro to look over your setup

(1) (2) (3) ... (1404) (1405) (1406) (1407) (1408) (1409) (1410) ... (1695) (Reply)

FTA Live Football Matches Announcement Thread / Free To Air Satellite Tv General Thread

Viewing this topic: QuoteJust1nce, jonescosmos, Edrizz(m), toscotech(m), Ferdiwar, tsiriman(m)

(Go Up)

Sections: politics (1) business autos (1) jobs (1) career education (1) romance computers phones travel sports fashion health
religion celebs tv-movies music-radio literature webmasters programming techmarket

Links: (1) (2) (3) (4) (5) (6) (7) (8) (9) (10)

Nairaland - Copyright © 2005 - 2024 Oluwaseun Osewa. All rights reserved. See How To Advertise. 75
Disclaimer: Every Nairaland member is solely responsible for anything that he/she posts or uploads on Nairaland.