Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by amarilo: 12:56pm On Apr 17, 2017
SolnergyPower:
Below is the information you requested for...

4kW System ( 5KVA Inverter)

1. 5KVA, 48V Pure Sine Wave Solar Inverter.

2. 4 x 200AH Premium Deep Cycle Batteries.

3. 8 x 250W Mono-crystalline Solar Panels.

4. 48V, 50A Charge Controller.

LOAD:
Sufficient to power the basic needs of a 4 bedroom home for up to 24 hours.

Enough energy to power all household loads including a Water Pumping
Machine and Pressing Iron and 1HP AC.

Please you may require more information to inform a decision on the plans above.

Thanks for the info. pls if you are to provide all these, how much will it cost me? Pls again will I need NEPA after I install this in my house. I don't want anything to with nepa and their crazy bills on darkness.
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by kiekie1(m): 11:14pm On Apr 17, 2017
URRY ! HIGH QUALITY SOLAR PANELS !!!

Yachi / YahSun Solar P-POLY,M-MONO
80w-P-25k
100w-P-30k
140w-M-42k
150w-P-43k
150w-M-45k
200w-M-60K
260w-M-75k
310w-M-85k
Stocks fast running low,call & place your order today
WhatsApp: O8I35O3I95I
SMARTCELL GLOBAL SERVICES
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by b2212(m): 11:26am On Apr 18, 2017
SolnergyPower:
1. I need to see the voltage and charge current (amperage) of the solar panel as shown in the attached picture.
2. You can load the output of the charge controller, but remember that, the output of the charge controller is only Direct Current (VDC).


thanks for the response. unfortunately i carelessly did not take a picture and it has now been installed on the roof.

i know it is 250W. on my solar controller when the sun is bright i have seen charge current as high as 11a.

what If i connect the output of to my inverter using a 2 output switch ?
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by SolnergyPower: 10:50pm On Apr 18, 2017
I have a 250W solar panel specification image attached to this post. Your specification should be within that range.

Since your inverter is 24V, your panels should have been connected in parallel thereby increasing your resultant charge current by a factor of 4.

There are factors that may be responsible for your low charge current of 11A at peak period.

a. The size of the cable that you used in connecting the solar panels to the charge controller. This must be a flex DC cable and should be at least 6mm. 10mm is better. The same size of cable that you used in connecting from the panels to the charge controller should be the same that is used to connect from the charge controller to the batteries terminals.
b. The orientation of your solar panels. The panels should directly face the sun at about 1:30pm.
c. Connecting the panels properly ie the panels should be connected in parallel in this case to have a higher charge current (amperage)

b2212:


thanks for the response. unfortunately i carelessly did not take a picture and it has now been installed on the roof.

i know it is 250W. on my solar controller when the sun is bright i have seen charge current as high as 11a.

what If i connect the output of to my inverter using a 2 output switch ?

b2212:


Great post here. I recently got 4 250w mono panels for my 24V, 1500VA inverter with 4 160ah batteries pics attached.
1. Hw long will it take to get a full charge
2. Can I connect anything to the load output on the controller

1 Share

Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by BlossomJey: 11:00am On Apr 19, 2017
PLEASE I NEED

*One 200W solar panels
*mppt solar charge controller

Heres my whatsapp
09096118861




SolnergyPower:
I have a 250W solar panel specification image attached to this post. Your specification should be within that range.

Since your inverter is 24V, your panels should have been connected in parallel thereby increasing your resultant charge current by a factor of 4.

There are factors that may be responsible for your low charge current of 11A at peak period.

a. The size of the cable that you used in connecting the solar panels to the charge controller. This must be a flex DC cable and should be at least 6mm. 10mm is better. The same size of cable that you used in connecting from the panels to the charge controller should be the same that is used to connect from the charge controller to the batteries terminals.
b. The orientation of your solar panels. The panels should directly face the sun at about 1:30pm.
c. Connecting the panels properly ie the panels should be connected in parallel in this case to have a higher charge current (amperage)



Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by b2212(m): 12:40pm On Apr 19, 2017
SolnergyPower:
I have a 250W solar panel specification image attached to this post. Your specification should be within that range.

Since your inverter is 24V, your panels should have been connected in parallel thereby increasing your resultant charge current by a factor of 4.

There are factors that may be responsible for your low charge current of 11A at peak period.

a. The size of the cable that you used in connecting the solar panels to the charge controller. This must be a flex DC cable and should be at least 6mm. 10mm is better. The same size of cable that you used in connecting from the panels to the charge controller should be the same that is used to connect from the charge controller to the batteries terminals.
b. The orientation of your solar panels. The panels should directly face the sun at about 1:30pm.
c. Connecting the panels properly ie the panels should be connected in parallel in this case to have a higher charge current (amperage)




I used 16mm flex cables all through. and the panels are flat on my roof. what is the ideal charge current for my type of installation.
Thanks for the responses
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by SolnergyPower: 1:03pm On Apr 19, 2017
a. Were the panels connected in series or parallel?
b. Did you use PWM or MPPT solar charge controller?
c. What is the voltage from the solar panels?

b2212:


I used 16mm flex cables all through. and the panels are flat on my roof. what is the ideal charge current for my type of installation.
Thanks for the responses
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by Kdude: 4:18pm On Apr 19, 2017
SolnergyPower:
It is usually written on the body of the inverter. Though you can also find it in the displayed parameters in the inverter if your inverter has a display screen.


Maximum current charge is 50A on the inverter and the charge controller is also 50A.

About increasing the panel:
Can two different wattage be used at same time in parallel.
Example: 150w and 250w
250w and 200w

Can mono and poly panels be used together as well.
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by SolnergyPower: 9:48pm On Apr 19, 2017
That means the inverter can have up to 50A from the solar charge controller.

You can combine solar panels but the resultant wattage, voltage and amperage will be that of the solar panel with lesser value.

You can use Monocrystalline and Polycrystalline solar panels together but you optimize them, please use an MPPT solar charge controller.

Kdude:


Maximum current charge is 50A on the inverter and the charge controller is also 50A.

About increasing the panel:
Can two different wattage be used at same time in parallel.
Example: 150w and 250w
250w and 200w

Can mono and poly panels be used together as well.
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by Kdude: 11:02am On Apr 22, 2017
SolnergyPower:


You can use Monocrystalline and Polycrystalline solar panels together but you optimize them, please use an MPPT solar charge controller.


Okay.
Are you advising I change from pmw to Mppt?

Do I necessarily need to ground/ earth my connection? If need be, the negative terminal goes the ground right? Or to earth the frame of the solar panel, inverter and then to the ground.
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by Kdude: 11:20am On Apr 22, 2017
@SolnergyPower
Solar Panel Specification

Wattage: 200W
Voltage: 36.6V
Charge Current: 5.46A

When you connect your two solar panels in parallel, you will have

Voltage: 36.6V. The Solar Charge Controller will take only 24V from here....
Charge Current: 10.94A (5.46A x 2)

[/quote]

I so much admire your patience with DIY.

Kindly help my understanding here...
Assuming the panels are working effectively; With the two panels in parallel now, am I to see 10.94A displayed on charge controller as calculated above or I will only see 5.46A displayed and assumed 10.94A is been delivered. (I tested the panels separately and both are working well).

Thank you.
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by SolnergyPower: 11:45am On Apr 22, 2017
You'll have 10.94A ideally but you may experience losses up to 30% or so.

Remember, you'll have that optimal value at when the sun is most intense and directly focused on your solar panels.

Kdude:
@SolnergyPower
Solar Panel Specification

Wattage: 200W
Voltage: 36.6V
Charge Current: 5.46A

When you connect your two solar panels in parallel, you will have

Voltage: 36.6V. The Solar Charge Controller will take only 24V from here....
Charge Current: 10.94A (5.46A x 2)



I so much admire your patience with DIY.

Kindly help my understanding here...
Assuming the panels are working effectively; With the two panels in parallel now, am I to see 10.94A displayed on charge controller as calculated above or I will only see 5.46A displayed and assumed 10.94A is been delivered. (I tested the panels separately and both are working well).

Thank you.

Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by SolnergyPower: 12:00pm On Apr 22, 2017
MPPT is more efficient though equally more expensive. When combining solar panels of different specifications, MPPT is the way to go.

Oga, DO NOT GROUND YOUR NEGATIVE TERMINAL!!!

Inverters have earthing connection, look for it and hook it to the earth of your house.

As for the panels, if your house has been properly earthed, you don't need to bother but if the panels are installed using frames, you need to buy earthing materials to earth the panels.

Kdude:


Okay.
Are you advising I change from pmw to Mppt?

Do I necessarily need to ground/ earth my connection? If need be, the negative terminal goes the ground right? Or to earth the frame of the solar panel, inverter and then to the ground.
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by perloomey(m): 7:24am On Jun 04, 2017
don't let this offer pass you by

Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by garbamaza: 7:12am On Jun 07, 2017
I need advice on panels array and charge controller appropriate for my luminous 2.5kva 36v with three 150ah batteries.
Thanks.
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by SolnergyPower: 8:39am On Jun 07, 2017
a. 36V, 30A Solar Charge Controller
b. 4 units of 250W Solar Panels

garbamaza:
I need advice on panels array and charge controller appropriate for my luminous 2.5kva 36v with three 150ah batteries.
Thanks.
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by garbamaza: 8:58am On Jun 07, 2017
[quote author=SolnergyPower post=57272791]a. 36V, 30A Solar Charge Controller
b. 4 units of 250W Solar Panels

The solar panels array 2x2 or in series?
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by SolnergyPower: 9:46am On Jun 07, 2017
2x2.

[quote author=garbamaza post=57273288][/quote]
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by spinola: 8:28am On Jun 28, 2017
Read before you buy a Mercury Inverter!


Mercury Inverter 2.4 KVA User Manual


www.mercurydirect.com.ng/mercury-inverter-2-4-kva-user-manual/

Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by SolnergyPower: 12:16pm On Jul 04, 2017
Sunshine Solar Panels For Sale (Wholesale Price) by SolnergyPower: 10:51am
Sunshine Solar Panels

Mono Price List

300w mono: ₦65,000
250w mono: ₦55:000
200w mono: ₦43,000
150w mono: ₦37,000
130w mono: ₦34,000
120w mono: ₦28,000
100w mono: ₦25,000
80w mono: ₦20,000

Poly Prices List

300w poly: ₦60,000
250w poly: ₦52:000
200w poly: ₦40,000
150w poly: ₦32,000
130w poly: ₦31,000
100w poly: ₦22,000
80w poly: ₦19,500

Call/WhatsApp: 0803-334-3911.
Solar@SolnergyPower.com
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by kunlef1: 1:04pm On Jul 16, 2017
@Pelumi

Do you repair both pure and modified sine wave inverter? I have both to repair, although in Lagos now, but can take it along when next I am in Ibadan.

perloomey:

250w solar panel is not enough to charge a 200ah adequately
let's do some mathematics
a battery is 12v 200ah= 2400wh
the battery can only give u 80% of it's life span which is 80% of 2400=1920wh
in Ibadan we've 4hours of good sun
so divide 1920/4= 480w
if u use 250w it will take close to 8hrs to charge a battery full
for more information contact me on 08068783141
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by kunlef1: 1:11pm On Jul 16, 2017
@perloomey

Can you provide the course outline or titles of what will be contained in the comprehensive Solar Power Training?

perloomey:
don't let this offer pass you by
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by zeestone99(m): 3:33pm On Jul 23, 2017
Call us for your neat and proffesional solar and inverter installations @affordable price.

Tel: 08117398294
Email :Info@monzpowersolutions.com
Facebook : http://facebook.com/monzpowersolutions

We also have renewable energy products in stock, such as inverters, battery, solar panels and charge controllers

Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by pointstores(m): 7:19pm On Jul 23, 2017
best Nigeria solar kit 700watts inverter 40ah battery 100watts panel free decoder with more than 100tv stations
total package is 140,000 no monthly payment
12volt 260ah 125,000 12volt 200ah 105,000 12volt 100ah 55,000 12volt 19ah 10,000 12volt 7ah 5,000 12volt 5ah 4,500
China Germany standard Jo power 12volt 180ah 75,000 Jo power 12volt 100ah 45,000
GMB Korea standard
200ah 90,000 100ah 42,000
location trade fair international mile 2 08166117634
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by osarodon(m): 4:43pm On Nov 14, 2017
Great information
SolnergyPower:
This is the order. Solar Panels >>>Batteries>>>Inverter. So inverters do not depend on solar panels. Rather, batteries do.

Solar Panel Charge Calculation
Power = Current x Voltage. Energy = Power x Time. So your 12V battery of 150Ah needs 1800Wh of energy (12 x 150). So a 25W PV panel would need 72 hours at full output (1800Wh/25W).

For a more accurate answer, you need a lot more information.

The output of the panel at any moment will depend on:

(1) the voltage, (which will be determined by the battery, and will change as the battery charges)

(2) the ambient temperature, and

(3) the amount light hitting the panel. The amount of light hitting the panel will depend on panel tilt, orientation, overshading, weather, altitude, location, time of year, time of day.

Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by osarodon(m): 5:07pm On Nov 14, 2017
Good
SolnergyPower:
Please check the back of the solar panels and to see a similar image attached to the post, snap it and post here.

We take your questions from there.
Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by osarodon(m): 5:25pm On Nov 14, 2017
Good work ���
SolnergyPower:
I have a 250W solar panel specification image attached to this post. Your specification should be within that range.

Since your inverter is 24V, your panels should have been connected in parallel thereby increasing your resultant charge current by a factor of 4.

There are factors that may be responsible for your low charge current of 11A at peak period.

a. The size of the cable that you used in connecting the solar panels to the charge controller. This must be a flex DC cable and should be at least 6mm. 10mm is better. The same size of cable that you used in connecting from the panels to the charge controller should be the same that is used to connect from the charge controller to the batteries terminals.
b. The orientation of your solar panels. The panels should directly face the sun at about 1:30pm.
c. Connecting the panels properly ie the panels should be connected in parallel in this case to have a higher charge current (amperage)



Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by oneshowguy: 11:09pm On Nov 14, 2017
LONG 12V 200 Amp WPL200-12BN 200Ah Rechargeable Sealed Lead Acid Deep Cycle Battery With Button Style Terminals

In Stock

CERTIFICATION - ISO9001, ISO14001,TL9000, CE, and UL Certified

BATTERY TYPE - 12V 200 Amp Rechargeable Sealed Lead Acid Deep Cycle Battery With Button Style Terminals

APPLICATION - Alarm System, Emergency Lighting System, Firefighting Equipment, Standby Power Supply and Telephone Switching System, Uninterrupted Power Supply, Telecommunication System, Computer Standby Power Supply System, Solar and Wind Power storage Etc....

RUGGED DESIGN - The battery case is made from a Non-Conductive ABS plastic, Strong Resistance to Shock, Vibration, Chemicals, Weather and Heat. Very easy to install and requires no maintenance.

BATTERY WEIGHT - 62KG

WARRANTY - At LONG, each battery has been strictly quality controlled. Each LONG Deep Cycle battery will come with a ONE year warranty. So you can purchase with confident.

LIFE SPAN - At 80% DOD 500 cycles / At 30% DOD 1400 cycles (4 to 5 years)

https://www.back2back.ae/wp-content/uploads/2017/07/WPL200-12BN-6.pdf

For any inquiry contact our Nigeria Sales Manager on Michael@back2back.ae or Whatsapp: 2348123329521

1 Like

Re: How To Install Solar Panels & Inverter For Home-step By Step Guide by ultrazone(m): 4:46pm On Jan 02, 2018
The truth is that solar is the way forward in Nigeria. I hope my country get to a stage when we can start looking into renewable energy sources as opposed to the problems that come with refining crude oil. God bless Nigeria.

Solar energy products

(1) (2) (3) (4) (5) (Reply)

Students Of White Plain British School Abuja Rattle Media With New Innovations / Locally Made Amphibian Jet Spotted At Lagos Stadium / What Kind Of Snake Is This?

(Go Up)

Sections: politics (1) business autos (1) jobs (1) career education (1) romance computers phones travel sports fashion health
religion celebs tv-movies music-radio literature webmasters programming techmarket

Links: (1) (2) (3) (4) (5) (6) (7) (8) (9) (10)

Nairaland - Copyright © 2005 - 2024 Oluwaseun Osewa. All rights reserved. See How To Advertise. 77
Disclaimer: Every Nairaland member is solely responsible for anything that he/she posts or uploads on Nairaland.