Welcome, Guest: Register On Nairaland / LOGIN! / Trending / Recent / New
Stats: 3,154,450 members, 7,823,061 topics. Date: Thursday, 09 May 2024 at 10:57 PM

Solar Energy, A Complement To FTA - Satellite TV Technology (1315) - Nairaland

Nairaland Forum / Entertainment / TV/Movies / Satellite TV Technology / Solar Energy, A Complement To FTA (2076750 Views)

UPS Back-up, Also A Complement To FTA / FTA Frequency / Cctv Installation A Complement To Fta And Solar Energy (2) (3) (4)

(1) (2) (3) ... (1312) (1313) (1314) (1315) (1316) (1317) (1318) ... (1701) (Reply) (Go Down)

Re: Solar Energy, A Complement To FTA by Pojomojo: 11:21pm On Dec 08, 2022
olopan:
For your setup, 50% of your loads are On & Off so that makes sense.

But I will suggest going for 6 pieces of 400W (Jinko, JA, Canadian, ERA, Yingli)

Assuming your inverter is a wide PV input inverter

For your battery reach out to Valto or a jos guy mentioned several times here.... You are sure to get warranty on the batteries.

You can call me with regards to having your setup built to standard, that suits your budget. My Contact is on signature

Please, what are you honest thoughts on this quote? 3.5kva
3kw 24volt Hybrid Inverter Setup + Solar

1. 3kw 24volt Hybrid inverter (80Amps MPPT) = #260,000

2. 12v 220AH battery 2pcs = #165,000 x 2 = #310,000 (Tubular battery)

3. 300watts Solar panels 6pieces (1.8kw) = #75,000 x 9 = #600,000

4. Solar mounting rails on roof and its accessories = #24,000

5. AC & DC Cables = #90,000

6. AC and DC breakers, MC4 connectors, Trunking, breaker box, Input AVS, DC Surge, ChangeOver. = #50,000

7. Logistics to site of work = #25,000
within Lagos

8. Installation = #60,000
Load
3 ceiling fan
10 sockets
15 bulb
One TV
One deep freezer and
Pumping machine
Re: Solar Energy, A Complement To FTA by TechGeek777: 12:29am On Dec 09, 2022
Pojomojo:
Please, what are you honest thoughts on this quote? 3.5kva
3kw 24volt Hybrid Inverter Setup + Solar

1. 3kw 24volt Hybrid inverter (80Amps MPPT) = #260,000

2. 12v 220AH battery 2pcs = #165,000 x 2 = #310,000 (Tubular battery)

3. 300watts Solar panels 6pieces (1.8kw) = #75,000 x 9 = #600,000

4. Solar mounting rails on roof and its accessories = #24,000

5. AC & DC Cables = #90,000

6. AC and DC breakers, MC4 connectors, Trunking, breaker box, Input AVS, DC Surge, ChangeOver. = #50,000

7. Logistics to site of work = #25,000
within Lagos

8. Installation = #60,000
Load
3 ceiling fan
10 sockets
15 bulb
One TV
One deep freezer and
Pumping machine

I am not an expert but I will give you my 2 cent.

1. You need state the name of the inverter

2. 165k * 2 should be 330k, unless the person is trying to cover up with other amount he quoted from other items. You are better off with LFP batteries.

3. He wrote 6 pieces panel and multiplied it by 9, then quote amount greater than what he's supplying. Unless this is a typo and you meant 8 pieces then this is manageable.

Gurus over to you.

3 Likes

Re: Solar Energy, A Complement To FTA by TechGeek777: 12:30am On Dec 09, 2022
olopan:
For your setup, 50% of your loads are On & Off so that makes sense.

But I will suggest going for 6 pieces of 400W (Jinko, JA, Canadian, ERA, Yingli)

Assuming your inverter is a wide PV input inverter

For your battery reach out to Valto or a jos guy mentioned several times here.... You are sure to get warranty on the batteries.

You can call me with regards to having your setup built to standard, that suits your budget. My Contact is on signature


Please who is the jos guy?
Re: Solar Energy, A Complement To FTA by durodee(m): 2:22am On Dec 09, 2022

1 Like

Re: Solar Energy, A Complement To FTA by TechGeek777: 5:31am On Dec 09, 2022
durodee:

That should be @Mantims

https://www.nairaland.com/390522/solar-energy-complement-fta/1040#105037581

Thanks, does he also sell grade A Eve coupled batteries like the one @valto sells?
Re: Solar Energy, A Complement To FTA by olopan(m): 6:29am On Dec 09, 2022
These are my personal thoughts

1. The quote has the barest minimum materials for the installation to work on paper

2. The prices quoted would get you average products, not that they are not good, just preference.

3. Ensure you know the exact warranty on each products .... Just to be save.

4. Lastly for your panels if you do 400W+ it will be helpful especially for your pump, as even 400W x 6 = around 1.5KWp under NoC.

Pojomojo:
Please, what are you honest thoughts on this quote? 3.5kva
3kw 24volt Hybrid Inverter Setup + Solar

1. 3kw 24volt Hybrid inverter (80Amps MPPT) = #260,000

2. 12v 220AH battery 2pcs = #165,000 x 2 = #310,000 (Tubular battery)

3. 300watts Solar panels 6pieces (1.8kw) = #75,000 x 9 = #600,000

4. Solar mounting rails on roof and its accessories = #24,000

5. AC & DC Cables = #90,000

6. AC and DC breakers, MC4 connectors, Trunking, breaker box, Input AVS, DC Surge, ChangeOver. = #50,000

7. Logistics to site of work = #25,000
within Lagos

8. Installation = #60,000
Load
3 ceiling fan
10 sockets
15 bulb
One TV
One deep freezer and
Pumping machine
Re: Solar Energy, A Complement To FTA by odimbannamdi(m): 7:18am On Dec 09, 2022
Guys, please can anyone recommend a wall mounted DC non-rechargeable fan that is very energy conservative?

Thanks
Re: Solar Energy, A Complement To FTA by sintolord(m): 8:04am On Dec 09, 2022
There are many out there. You can go with Qasa. Reason, if it becomes faulty, it can easily be repaired at Arena, Oshodi

odimbannamdi:
Guys, please can anyone recommend a wall mounted DC non-rechargeable fan that is very energy conservative?

Thanks
Re: Solar Energy, A Complement To FTA by ozone0801(m): 8:32am On Dec 09, 2022
Trippledots:
Hi,
I have 2 brand new Jinko 470W panels for urgent sale #100k/pc.
Location is isolo-ejigbo on the mainland.
Monocrystaline panels.

Still available?
Re: Solar Energy, A Complement To FTA by jonescosmos: 9:32am On Dec 09, 2022
Good morning beautiful people.

Abeg who has this kind of Din Rail DC Energy Meter?

Re: Solar Energy, A Complement To FTA by odimbannamdi(m): 9:57am On Dec 09, 2022
sintolord:
There are many out there. You can go with Qasa. Reason, if it becomes faulty, it can easily be repaired at Arena, Oshodi


Thanks for the response, boss. Yes, Qasa tops my list, but I can't seem to find any of their product that is wall-mounted. Perhaps I am not looking well enough. This is an example of what I mean by wall-mounted

Re: Solar Energy, A Complement To FTA by isangjohnson: 10:29am On Dec 09, 2022
durodee:

That should be @Mantims

https://www.nairaland.com/390522/solar-energy-complement-fta/1040#105037581
Oga someone needs your contact for urgent issues.
Re: Solar Energy, A Complement To FTA by zeestone99(m): 12:48pm On Dec 09, 2022
ewizard1:
Good evening House, anyone have a clean functional 80A Epever Charge Controller for sale in Lagos?

Brand new Epever 100a available - 260k
Re: Solar Energy, A Complement To FTA by zeestone99(m): 12:51pm On Dec 09, 2022
Pojomojo:
Please, what are you honest thoughts on this quote? 3.5kva
3kw 24volt Hybrid Inverter Setup + Solar

1. 3kw 24volt Hybrid inverter (80Amps MPPT) = #260,000

2. 12v 220AH battery 2pcs = #165,000 x 2 = #310,000 (Tubular battery)

3. 300watts Solar panels 6pieces (1.8kw) = #75,000 x 9 = #600,000

4. Solar mounting rails on roof and its accessories = #24,000

5. AC & DC Cables = #90,000

6. AC and DC breakers, MC4 connectors, Trunking, breaker box, Input AVS, DC Surge, ChangeOver. = #50,000

7. Logistics to site of work = #25,000
within Lagos

8. Installation = #60,000
Load
3 ceiling fan
10 sockets
15 bulb
One TV
One deep freezer and
Pumping machine

Ask for the brands of materials
Re: Solar Energy, A Complement To FTA by Kabawhat: 2:04pm On Dec 09, 2022
.
Re: Solar Energy, A Complement To FTA by Kabawhat: 2:04pm On Dec 09, 2022
Please guys please I need your suggestion I just move to a new remote location am planning to go off grid


I have my batteries and solar panels and solar controller on ground but am still saving to buy get inverter

Most of my electric appliances are all optimized for DC (fans, bulb and other all 12V) don't know if a good ideal to can run DC 12V battery current through into AC 220v wire since most of the appliances are 12V best saving up to inverter please


Running DC 12 voltage into AC 220V cable before buying inverter
Re: Solar Energy, A Complement To FTA by Barezzi(m): 4:36pm On Dec 09, 2022
Guys, Is there anyone with a 1000 amps Victron Lynx Shunt - VE.CAN?
Re: Solar Energy, A Complement To FTA by mctfopt: 6:03pm On Dec 09, 2022
Kabawhat:
Please guys please I need your suggestion I just move to a new remote location am planning to go off grid


I have my batteries and solar panels and solar controller on ground but am still saving to buy get inverter

Most of my electric appliances are all optimized for DC (fans, bulb and other all 12V) don't know if a good ideal to can run DC 12V battery current through into AC 220v wire since most of the appliances are 12V best saving up to inverter please


Running DC 12 voltage into AC 220V cable before buying inverter

The best you could hope for is to run some very low wattage (not even up to 100w) DC load off the DC load section off your solar charge controller or... getting elcheapo inverter (see attached image) pending when you are good for getting a better one?

Note: Don't run DC voltage for AC appliance. Not a good idea.

Re: Solar Energy, A Complement To FTA by tsiriman(m): 6:37pm On Dec 09, 2022
Hello house please what is the next best Hybrid Inverter after Deye?

Or a list of good Hybrid inverters one can buy if Deye is too expensive?
Re: Solar Energy, A Complement To FTA by isangjohnson: 6:53pm On Dec 09, 2022
tsiriman:
Hello house please what is the next best Hybrid Inverter after Deye?

Or a list of good Hybrid inverters one can buy if Deye is too expensive?
You may consider Growatt ES but I guess idle power consumption is up to 60w for 5kw 48v.
If you're working on budget and 5kw 48v system is your target, then I'll advise you grab one Felicity from Jonescosmos. What trip me for that system is the idle power consumption/the efficiency.

1 Like

Re: Solar Energy, A Complement To FTA by AshipaEk0: 8:03pm On Dec 09, 2022
Please give me tips on wiring this AC/DC fan for AC use.

Its rather confusing and the 1 page manual it comes withis not helpful

Re: Solar Energy, A Complement To FTA by zeestone99(m): 8:15pm On Dec 09, 2022
tsiriman:
Hello house please what is the next best Hybrid Inverter after Deye?

Or a list of good Hybrid inverters one can buy if Deye is too expensive?

You can do growatt, sorotec or sunmart.

Sorotec Revo Vmii 5.5kw 48v 100a hybrid inverter 500vdc - 420k

Sorotec Revo Vmii 3.5kw 24v 100a hybrid inverter 500vdc - 350k

Sorotec 5.5kw 48v 100a hybrid inverter 500vdc parallel version (includes parrallel kit) - 450k

Sorotec 3.5kw 24v 100a hybrid inverter 500vdc parallel version (includes parrallel kit)- 380k

Sorotec vmiii 3.5kw 24v 100a hybrid inverter 500vdc - 340k

Sunmart vmii 5.5kw 48v 100a hybrid inverter 500vdc - 375k

Sunmart Vmii 3.5kw 24v 100a hybrid inverter 500vdc - 320k

Sunmart Vmiii 3.5kw 24v 100a hybrid inverter 500vdc - 340k

Sunmart Vmiii 5.5kw 48v 100a hybrid inverter 500vdc - 395k

Call/chat - 08117398294
09067411214
Re: Solar Energy, A Complement To FTA by tsiriman(m): 8:38pm On Dec 09, 2022
isangjohnson:

You may consider Growatt ES but I guess idle power consumption is up to 60w for 5kw 48v.
If you're working on budget and 5kw 48v system is your target, then I'll advise you grab one Felicity from Jonescosmos. What trip me for that system is the idle power consumption/the efficiency.

Thank you
Re: Solar Energy, A Complement To FTA by tsiriman(m): 8:38pm On Dec 09, 2022
zeestone99:


You can do growatt, sorotec or sunmart.

Sorotec Revo Vmii 5.5kw 48v 100a hybrid inverter 500vdc - 420k

Sorotec Revo Vmii 3.5kw 24v 100a hybrid inverter 500vdc - 350k

Sorotec 5.5kw 48v 100a hybrid inverter 500vdc parallel version (includes parrallel kit) - 450k

Sorotec 3.5kw 24v 100a hybrid inverter 500vdc parallel version (includes parrallel kit)- 380k

Sorotec vmiii 3.5kw 24v 100a hybrid inverter 500vdc - 340k

Sunmart vmii 5.5kw 48v 100a hybrid inverter 500vdc - 375k

Sunmart Vmii 3.5kw 24v 100a hybrid inverter 500vdc - 320k

Sunmart Vmiii 3.5kw 24v 100a hybrid inverter 500vdc - 340k

Sunmart Vmiii 5.5kw 48v 100a hybrid inverter 500vdc - 395k

Call/chat - 08117398294
09067411214

Thank you, appreciate
Re: Solar Energy, A Complement To FTA by Kabawhat: 8:45pm On Dec 09, 2022
mctfopt:


The best you could hope for is to run some very low wattage (not even up to 100w) DC load off the DC load section off your solar charge controller or... getting elcheapo inverter (see attached image) pending when you are good for getting a better one?

Note: Don't run DC voltage for AC appliance. Not a good idea.


All the appliance are actually DC 12v

Am thinking of connecting directly to the battery ooooh
Re: Solar Energy, A Complement To FTA by jonescosmos: 9:16pm On Dec 09, 2022
There are other several low budget devices that can help you act as a DC low voltage cut-off anyway.



Kabawhat:
Please guys please I need your suggestion I just move to a new remote location am planning to go off grid


I have my batteries and solar panels and solar controller on ground but am still saving to buy get inverter

Most of my electric appliances are all optimized for DC (fans, bulb and other all 12V) don't know if a good ideal to can run DC 12V battery current through into AC 220v wire since most of the appliances are 12V best saving up to inverter please


Running DC 12 voltage into AC 220V cable before buying inverter

Nice to run your loads on DC source but how do you intend to protect your battery from discharging below Cut-off voltage?

My answer to that is: Get this kind of ATS that has the ability to cut-off the DC load if bettery voltage drops below set point. This way you can enjoy a longer life span from your batteries because you basically will not endagner them by dischasrging them below the set Cut-Off voltage that you will set. See attached picture.

It is not an inverter but just a transfer switch. You can actually use two battery banks as your sources. Battery A goes below cut-off point, your load gets transfered to Battery B.

1 Like

Re: Solar Energy, A Complement To FTA by jonescosmos: 9:17pm On Dec 09, 2022
More

Re: Solar Energy, A Complement To FTA by jonescosmos: 9:28pm On Dec 09, 2022
Digital Low Voltage Protector Disconnect Switch Cut Off 12V Over-Discharge Protection Module for 12-36V Lead Acid Lithium Battery Low Voltage Cut-off for OVER DISCHARGE PROTECTION.

You can freely set the discharging mode and set parameters. For example, when the battery voltage reaches the set voltage, the module will automatically disconnect to avoid battery over-discharging and prolong battery life.
It has MEMORY FUNCTION With power-off protection, it will save your setting when power off suddenly.
Also has DELAY TURN-ON That means, after a disconnect, the interval between turning on again. The time range that can be set is 0-999 seconds.


Kabawhat:



All the appliance are actually DC 12v

Am thinking of connecting directly to the battery ooooh

2 Likes

Re: Solar Energy, A Complement To FTA by Trippledots(m): 9:30pm On Dec 09, 2022
Pojomojo:
is this your last price? Full picture of the panel
Sold
Re: Solar Energy, A Complement To FTA by Kabawhat: 10:20pm On Dec 09, 2022
jonescosmos:
More

Price sir
Re: Solar Energy, A Complement To FTA by jonescosmos: 10:57pm On Dec 09, 2022
Re: Solar Energy, A Complement To FTA by durodee(m): 1:00am On Dec 10, 2022
I have been replying the mail request.s
Let's chat on 07zero-852-688four2

isangjohnson:

Oga someone needs your contact for urgent issues.

(1) (2) (3) ... (1312) (1313) (1314) (1315) (1316) (1317) (1318) ... (1701) (Reply)

FTA Live Football Matches Announcement Thread / Free To Air Satellite Tv General Thread

Viewing this topic: Hero2t, Ferdiwar, jmaine

(Go Up)

Sections: politics (1) business autos (1) jobs (1) career education (1) romance computers phones travel sports fashion health
religion celebs tv-movies music-radio literature webmasters programming techmarket

Links: (1) (2) (3) (4) (5) (6) (7) (8) (9) (10)

Nairaland - Copyright © 2005 - 2024 Oluwaseun Osewa. All rights reserved. See How To Advertise. 58
Disclaimer: Every Nairaland member is solely responsible for anything that he/she posts or uploads on Nairaland.