Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 9:03pm On Jan 24, 2022 |
Thunderbolt: Trying to decide between the following: 1. A conventional psw inverter + separate mppt charge controller 2. A hybrid inverter with built-in mppt charge controller
Read a little about the advantages and disadvantages of TL inverters. What stood out for me was talk of being more susceptible to surge issues.
For those who have experience with these inverters, pls what are the practical issues I could face using a hybrid, and how could I mitigate against these issues?
Thanks Any disadvantage you have with Stand alone apply to Hybrid.. I asked an installer same question sometimes ago.. he said if Charge controller fails or Inverter fails you can continue to use one of them.. I was not convinced, I went for Hybrid.. because of Priority settings, Inverter charge from same source, Ease of installation.. less cable losses.. somewhat cheaper.. Reason most also go for Stand alone was that, then External CC was more efficient.. compared to inbuilt PWM on Hybrid, But Hybrid already catch up with inbuilt MPPT even offer High VOC input.. As it stands Hybrid is the first choice.. |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 7:07am On Jan 24, 2022 |
deking: Why do you need a breaker though seeing the inverter already supports voltage in excess of what you can possibly generate. The concept of DC breakers was prevalent when maximum VOC supported by charger controllers was about 150v Always Read Manual before you Install your inverter and do as recommended. Breakers are for protection and Isolation.. How do you limit VOC with Breakers? Manufacturer recommends breakers or Fuse.. |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 2:01pm On Jan 21, 2022 |
carreport: Growatts SPF 5000 ES has its inbuilt mppt as 450vdc 18a
I intend to connect my 20nr 300watts Canadian solar panels in 10S2P.
The VOC of the panels is 38vdc So 10s is about 380v
I have been looking for suitable breaks for the input
450v 20a breaker but all I see in the market is 500vdc 63a
Please size of breaker is suitably sized for 450vdc 18a input? Get breaker from AliExpress.. https://a.aliexpress.com/_vEm4P525A 500V |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 1:18pm On Jan 20, 2022 |
primefaith1: [b]150w panel is 45k. [/b]The one from Jumia will still be sourced from Alaba. I will advice, you go to Alaba and get it yourself. People run deliveries to Ajah axis 3 times weekly and will cost you less than 3k. That's too expensive... Is it Originally Canadian Solar? |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 4:05pm On Jan 18, 2022 |
olopan: Kindly check through your post, maybe a typographic error Sorry, this is what I meant... Input of Both inverter must be connected together as well as Output of both inverter, must be connected |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 7:33am On Jan 18, 2022*. Modified: 4:07pm On Jan 18, 2022 |
carreport: Yes the Growatt 5kva hybrid inverters come with paralleling kit and their manual shows that the AC output can be combined.
I just want to be triple sure since I haven't seen it done before Since you have the wiring diagram and all the accessories, Simply wire accordingly, AC input and Output must be connected together, batteries must be connected to same bank. Do all this before switching on the Power on the inverter. UpdateThat I meant in Bolded is Input of Both inverter must be connected together as well as Output of both inverter, must be connected |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 12:14am On Jan 17, 2022 |
joshdgr8: For Any Of this Growatt Inverter Product Contact Me (All in Stock Except Some)
Growatt 3KW/24V TL Growatt 3KW/48V TL Growatt 5kw/48v HVM Growatt 3.5kw/48v SPF ES(Batteryless) Growatt 5kw/48v SPF ES(Batteryless) Growatt 6KW/48V Growatt 8KW/48V Growatt 10KW/48V Growatt 12KW/48V
All Inverter size has Inbuilt MPPT Charge Controller
Lithium Batteries
Pylontec Lithium-ion Battery – US 2000 48v/2.4kwh Pylontec Lithium-ion Battery – US 3000C 48v/3.6kwh
Growatt Hope 3.3L Lithium battery 3.3kwh/48v
Chat Me Up for Price List and Cost o7o35158237 or o7o11663917 Please state it on the list.. rather than complicating things.. |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 12:11am On Jan 17, 2022 |
carreport: Good evening Please I need help in making up my mind on which lithium battery to buy. I'm doing an upgrade and an overhaul so I want to get it rite from the start.
1. Felicity 10kw battery Or 2. Tactel 15kw
They are almost same in price.
Does Tactel have an office in Nigeria like felicity?
PS: which of them will work better in terms of communication with Growatt inverters
Thank you all Go all Felicity inverter and Batteries, they should have sort of communication in their newer models.... Contact the company and state your need, they will provide recommendations.. Tactel, not sure |
Phones › Re: Does Switching Off Mobile Data Minimized Data Consumptions? by Dam5reey(m): 3:41pm On Jan 16, 2022 |
Eaglesence: Abeg my dears. Which is the best phone to go for that will beat hackers attempts? A list from the best will be appreciated Pixels Phones, You get Monthly Security updates... Reason I use Pixel 4a, since Iphone is currently on the high side.. |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 3:32pm On Jan 16, 2022 |
funshyboi: Hello guys I noticed these line traces all over my solar panel. What does it mean ?
Or could it be the reason why I’ve been having low amp supply lately? The Cell at the edge seems to be broken, that Panel will great affect your harvest especially if it's connected in series with some panels.. It's like having a shade on the panel.. Anyways investigate further.. Check the Voltage output on the panel.. |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 7:16am On Jan 16, 2022 |
smallsmall: Gurus, one question.
Can one mix together (charging and usage), two battery Banks of, 1) LiFePo4 Pristmatic Cells 2) and the other LiFEPo4 32650 Cells, if both are of the same Capacity (3kW each) and connected to the same Hybrid Inverter? To form 6KW Battery Bank. Any downside, danger? You are good to go, Since you have same capacity. Connect in parallel with the same cable length to inverter or use Bus bars.. |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 7:09am On Jan 16, 2022 |
ceaser: Before now I believed that dry season dust on solar panels do not have SIGNIFICANT negative impact on insolation. But I got tired of the suboptimal output from my array and contracted the services of a carpenter to help climb the roof and do the cleaning.
Done early in the morning, the picture shows the before cleaning, at 25% cleaning and at 50% cleaning of the array. Dem never even reach 100% sef.
162w to 347w to 665w 
I don't need any more convincing. You have more than Dust on your panels, Dust will only reduce by 10-15%.. You simply have bird poo or something similar, that's causing shade and not Dust, Shading is more worse than Dust.. This season is also different sha.. seems Dust is thicker..  |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 8:23pm On Jan 15, 2022 |
samnaija: Thanks for info , it's on the high side. I don't blame the client for sticking with LA. Make this prices come down then we can port. Wait a moment how much is 8 12V Quanta batteries?? Compared to 1.4M Considering that you won't change batteries in 10 years.. |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 11:46am On Jan 15, 2022 |
Valto: it is approximately 2million, assuming u are going the DIY way. that is 32pcs of 200ah lifepo4 cells with good bms. Way I see it is that he want to replace those Quanta Lead Acid.. with Lifepo4 equivalent.. The 8 LA is 19.2KWH, 9.6KWH Usable. 50% DOD 16, 280AH, 14.3KWH, 11.4KWH Usable. 80% DOD 8 LA can easily be replaced with 16 of 280AH cells If he want to match usage capacity a 16 Lifepo4 cells will only take the space of 2 Quanta 1.4M should do a perfect DIY build32 of 200AH if he want to match exact capacity.. 20KWH, 16KWH usable |
Properties › Re: 4 Units Of 200AH Inverter Batteries At Giveaway Price by Dam5reey(m): 7:13am On Jan 14, 2022 |
SolarEdge: Tested and certified inverter batteries available to setup a low budget inverter / solar system.
3 units of 200AH ritar batteries and a unit of 200AH Luminous
PRICE: #65,000 NON NEGOTIABLE
we also have used Canadian solar panels
Call/watsapp: 07038567494 How much is your Canadian Solar and what size? |
Phones › Re: Does Switching Off Mobile Data Minimized Data Consumptions? by Dam5reey(m): 1:15pm On Jan 09, 2022 |
lifezone247: So often people tend to switch off their mobile data. Most times they will tell you they want to preserve their data, some actually did it to preserve battery consultations anyway. But does switching off mobile data actually preserved data usages? Mine is always on 24/7. It does not, it may limit you from browsing and using data anyhow, It only saves battery... Once you on data it will synchronize all the Notifications you missed.. |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 9:44am On Jan 06, 2022 |
queenfav: Good morning house,pls we recently did a 4 battery setup.It's Mpower 220ah indian battery. On our Kartel inverter , the Voltage at Nepa Full charge (100%) is 56.8v
On our Epever charge controller,it's 57.3v.My confusion is how to know the 50% DOD voltage for the battery so i won't allow it drain below that. You can set the Cut off to 48V, SOC is hard to determine on Lead acid unlike the Lifepo4, where BMS tells you. If you are willing to add this device it will help determine SOC.. This one has Monitor and Bluetooth https://a.aliexpress.com/_vUlBG1NGN 11,254.46 53%OFF | Battery Monitor KL-F DC 0-120V 100A 400A 600A Battery Tester Voltage Current Meter Battery Coulomb Meter Capacity Indicator https://a.aliexpress.com/_vdfs2vThis one your Phone is the monitor via Bluetooth |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 9:39am On Jan 06, 2022 |
OkoroPeugeot: So after connecting I'm getting 76v with multimeter at the panel
76v also at the wires before I connect them to the controller.
When I connect it to the controller it shows 73v as it starts then reduces to 29/30v and starts charging.
Now I'm confused. I'm getting 15/17w this morning. Which MPPT you got? Your batteries voltage is 12 or 24V.. Something is wrong obviously with the panel.. |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 1:14pm On Jan 05, 2022 |
OkoroPeugeot: So I got an MPPT controller
It charges now but I noticed the highest power I'm getting from two 250w panels connected in parallel is 150w (Around 12pm)
How much is a genuine 300w panel from source? You have MPPT, put them in series, you can get 250w for around 55k.. |
Technology Market › Re: House Clearance Sales.. Come In Here!!!! by Dam5reey(m): 3:20pm On Jan 03, 2022 |
Dam5reey: [s]Neatly used 24V, 2.4KW Hybrid MPPT 25A, 102VOC, 1000w PV input Pure Sine Wave
100k Price drop 90k Still available Manufactured March 2021
Negotiable[/s] Sold |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 8:39am On Dec 31, 2021 |
smallsmall: Good Morning House.
Does anyone have an idea of how l can 'wake up' a LifePo4 Battery bank (DIY), without the use of a Light Board
or alternatively, where l can get a light board, without having to order it all the way from China?
Thanks in advance Do you have access to the BMS, please send Model.. You can wake up with Resistor or Charge source too.. |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 8:16am On Dec 30, 2021 |
ceaser: How do we know the respective authorised dealer, biko? At least for those of us far from Lagos and with no luxury of doing window shopping there. Felicity, Yingli, etc.. just visit their website as for local authorii dealer.. |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 8:14am On Dec 30, 2021 |
ceaser: Abeg Ojes, LFP price don come down? Because I used to know 12v/100ah to be around 140k to 150k o.
It's like you forgot to calculate the price of BMS and enclosure with it.
This is seriously annoying. This is even worse than being sold a lemon. Why not let a client know the options available and then let them make an informed choice? Sadly we can't purchase panels directly ourselves from overseas or even buy solar cells and DIY like it can be done with Lithium batteries. It would have cut down chances of falling into the hands of these fraudsters.
Inverters, Lithium cells, controllers, switches, meters can all be personally ordered from reputable manufacturers and bypass fraudulent middle marketers. But solar panels, no hope yet.
I guess we still have to hope reputable dealers maintain their reputation and sincerity. It's possible to buy from Alibaba, if you are willing to spend the money.... |
Technology Market › Re: House Clearance Sales.. Come In Here!!!! by Dam5reey(m): 9:03am On Dec 29, 2021 |
Neatly used 24V, 2.4KW Hybrid MPPT 25A, 102VOC, 1000w PV input Pure Sine Wave
100k Price drop 90k Still available Manufactured March 2021
Negotiable 0813-239-4478
|
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 8:34am On Dec 29, 2021 |
OkoroPeugeot: This is it With this specs if your batteries barely charge, then your Panel is 150w in disguise  Your PWM should be Auto Voltage detect that is it will switch to 24V when you connect 24v batteries, if not check your battery voltage is on 24V... Disconnect everything, Connect Batteries only first, set to 24V then connect Panels last then observe again.... And during your observations was there load on the Batteries, if yes disconnect all load then charge battery without load |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 8:26am On Dec 29, 2021 |
OkoroPeugeot: For those with experience using budget PWM controllers
I had a setup with 24v panel and 12v battery with a 30A pwm controller.
It was working properly but I read charging would be faster from here if everything matches so I got a 24v inverter and 24v battery.
Normally the arrow on the controller blinks but now in the morning the panel icon comes up and the arrow just stays steady and the battery voltage barely increases all day.
The controller has 12/24v so I'm confused. Has anybody experienced this?
(ps. I know I should upgrade to mppt and would do that when I get funds or an mppt fan dashes me Send the Specs sheet at the back of the panels.... |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 11:06pm On Dec 28, 2021 |
temmyt20: Good evening house. Any expert in the house that can assist with a quote for a solar setup with 100ah battery. Inverter of 500w Solar panel. Setup will be used to power appliances not up to 100watts Budget 200k.. |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 5:52pm On Dec 27, 2021 |
odimbannamdi: Thanks for the clarification, Oga Sintolord. .it definitely varies from inverter to inverter and not a given for ALL inverters. What just took me off was the assertive tone with which he took the position, and the whole terminology mix up. I honestly was beginning to get worried coz I don't don't a large battery bank like most of our Ogas here... ..Make my meter land so that I can perform my own test.
Thanks again for your contribution. Honestly, I am not proving right or Wrong.. I am open to New discovery too.. As you can see, Na Third party helped out in clearing the air.. I was partially correct with proofs... See I have Energy meter, Bench power supply, but I no get energy to repeat test I have done several times... |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 5:38pm On Dec 27, 2021 |
odimbannamdi: Thanks for the clarification, Oga Sintolord. .it definitely varies from inverter to inverter and not a given for ALL inverters. What just took me off was the assertive tone with which he took the position, and the whole terminology mix up. I honestly was beginning to get worried coz I don't don't a large battery bank like most of our Ogas here... ..Make my meter land so that I can perform my own test.
Thanks again for your contribution. I already explained this yesterday.. ✌️ |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 10:45am On Dec 27, 2021 |
ewizard1: Good morning.
So based on the drag about "Idle Consumption" and "No Load Consumption" 
Just got to the workshop now and I'm about to make a test now. A bench power supply as the Battery and my 24v 800/1600w PSW Transformerless inverter.
Not sure if I can upload a video directly here. If not, I'll do very good pictures.
cc Dam5reey , Dollarnaira
*** seems uploading video directly isn't possible here. I dont have a YT channel. Would lookup a way to present a video. Thanks a lot, Just like the spec sheet states < 0.5 A |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 9:50pm On Dec 26, 2021 |
dollarnaira: Are u humble enough to know that you rude? Go jor!!! I am Rude just because I pointed out an error, I accept, I am rude sir!!! Please remove the 1w claim, since a third party already clarify, that's the only issue we have now.. So you don't misleading people into buying the cheap inverter because of your post!! Taink u... |
Satellite TV Technology › Re: Solar Energy, A Complement To FTA by Dam5reey(m): 9:26pm On Dec 26, 2021 |
AndroBlaze: Bro I once made the same mistake you made, using my AC wattmeter to give me the idle consumption of my inverter, which came out negligible before it now dawned on me that there was no way an ac meter plugged into the inverter would be able to measure the dc amps that the same inverter was pulling from my battery.
I ended up getting a DC meter & shunt and voila I found out my old school inverter was pulling 20-28 wats on my battery for simply being on!! Thats 2amps down the drain and like Dam5reey pointed out its probably gets higher depending on how high the load it is benchpressing becomes.
Nowadays, my dc meter is used to determine all load, I hardly use the ac for anything.
Its clear that you were just honestly asking and he (for some reason) just couldn't seem to decipher that you were being honest in understanding your mistake.
Let it be and take the claim off.
@Dam5reey, pls look at the tone of people when you reply, he was being sincere and this could have been cleared up in just one post really, if you had noticed the sincerity. Be calming down. Lol, It's someone that does not want to learn that would take my reply personal, he should be humble enough to accept that the 1.1w is Wrong. |